popic ®   16-Mar-2023 13:54

LNG Ship 2022 No4 CT No2 Cargo Pump trip_LLB


Year: 2022
Language: english
Author: Gaslog
Genre: Documentation
Format: PDF
Quality: eBook
Pages count: 13
Description: On March 19th, 2022, the subject vessel was at Ningbo Zhejiang, LNG Terminal, and cargo discharging operations were ongoing.
Weather condition: Overcast Sky/ Gentle Breeze / Slight Sea / NW 3.
At 21:19 LT, the No2 Main Cargo pump in Cargo Tank No 4 tripped while it was running normally in parallel with the rest of the cargo pumps at full capacity discharging rate. The incident was reported to the Gaslog duty officer and charterers as per SMS & CP procedures.
The immediate cause of the trip was 2 power protection fuses that have been found blown out in the pump’s electric motor vacuum breaker cubicle.
The location of the breaker and cubicle is in the No2 High Voltage Cargo Switchboard.

Contents

Screenshots

No4 CT No2 Cargo Pump trip_LLB.pdf

Download [1 KB]

Thank U
Reply
refresh list

Similar releases

H869R HV Power Distribution System and Propulsion Drive Course - ABB [2018, PDF]
NMC 29: 6.6kV High Voltage Generating Plant Training - NYK Maritime College [2007, PPT]
Cargo pumps and related systems in M/T - ΣΑΡΑΦΟΠΟΥΛΟΥ ΑΓΓΕΛΙΚΗ [2018, PDF]
PSC deficiency Cards - RINA [2002, PDF]
Crude oil tanker "British Kestrel" Cargo operating manual - Worldwide Marine Technology…
Ship Inspection Report (SIRE) Programme VIQ Rev 1.2 - OCIMF [2016, PDF]
Bulk Carriers - Guidance and Information on Bulk Cargo Loading and Discharging to Reduce the…
Framo Service Manual For Cargo Pumping System - Frank Mohn Services AS [2005, PDF]
Sea Empress Grounding - MAIB [1996, PDF]
Pumping cargo - Glenn Lundstrom [1994, PDF]
LOAD MORE